Threaded rod load table: M6 to M20 studding capacity

Updated 7 min readStrutconfigurator · NEXTRIQ

Short answer

Threaded rod capacity is the tensile stress area times the yield strength, divided by a safety factor. With a factor of 2, M10 grade 4.8 studding carries about 9.3 kN (roughly 950 kg) and M12 about 13.5 kN. The anchor, channel nut or beam clamp is nearly always weaker. Strutconfigurator shows these values as indicative.

A threaded rod load table tells you how much tension a rod can safely carry before you size the anchors, channel and beam clamps around it. The figures below cover M6 to M20 studding in grades 4.8 and 8.8. They come from the tensile stress areas in BS EN ISO 898-1 and a stated safety factor, so you can check every number yourself.

Threaded rod, called studding on most UK sites and allthread in the US, is steel bar threaded along its full length. It is supplied to DIN 976-1, which replaced DIN 975, typically in 1, 2 and 3 metre lengths [1][6].

What load can M6 to M20 threaded rod carry?

Size Pitch (mm) As (mm²) 4.8 (kN) 4.8 (kg) 8.8 (kN) 8.8 (kg)
M6 1.0 20.1 3.2 330 6.4 660
M8 1.25 36.6 5.9 600 11.7 1,190
M10 1.5 58.0 9.3 950 18.6 1,890
M12 1.75 84.3 13.5 1,370 27.0 2,750
M16 2.0 157 25.1 2,560 50.2 5,120
M20 2.5 245 39.2 4,000 78.4 7,990

Coarse pitch to ISO 261 [3], tensile stress area As to ISO 898-1 [2]. Capacity: rule of thumb, indicative; the manufacturer confirms. Formula: F = As × Re / 2, pure tension at room temperature.

Read this as the limit of the rod on its own. It assumes a straight rod in pure tension, full thread engagement in every nut, no welding and no fire rating.

How do you calculate threaded rod capacity yourself?

You need three inputs.

  1. Tensile stress area As. This is the effective area of the thread from ISO 898-1 [2], and it is smaller than the plain bar. An M10 has a gross area of 78.5 mm² and a stress area of 58.0 mm², which is 26% less (calculated).
  2. Yield strength Re. The property class tells you. The first digit times 100 gives the nominal tensile strength in N/mm². The second digit times 10 gives the percentage of that at which the steel yields. Grade 4.8 therefore means 400 N/mm² tensile and 320 N/mm² yield. Grade 8.8 means 800 and 640 N/mm² [2].
  3. Safety factor. The table uses 2 as a first indication. Manufacturers apply their own factors and reductions.

Worked example, M10 grade 4.8:

  • 58.0 mm² × 320 N/mm² = 18,560 N
  • divided by 2 = 9,280 N, rounded to 9.3 kN
  • 9,280 N / 9.81 = about 946 kg

The threaded rod load calculator uses the same formula if you want to try other sizes.

How does the rule of thumb compare with manufacturer data?

One manufacturer publishes a maximum tensile load for hot-dip galvanised grade 4.8 rod, using a safety factor of 1.7 [6]. Side by side:

Size Rule of thumb 4.8, factor 2 (kg) Manufacturer 4.8 HDG, factor 1.7 (kg) Weight (kg/m)
M6 330 365 0.177
M8 600 669 0.319
M10 950 1,066 0.500
M12 1,370 1,554 0.725

Manufacturer data [6], indicative; the manufacturer of your support system confirms.

The rule of thumb sits roughly 10 to 12% below the published figures (calculated). That keeps a first design on the safe side. For the quotation, use the table of the supplier you will actually install.

Which grade should you specify: 4.8, 8.8 or stainless?

Class Tensile Rm (N/mm²) Yield Re or Rp0.2 (N/mm²) Typical use Standard
4.8 400 320 Standard indoor hangers, galvanised ISO 898-1 [2]
8.8 800 640 Heavy loads, or a smaller rod size ISO 898-1 [2]
A2-70 / A4-70 700 450 Stainless 304 or 316 in damp, hygienic or marine areas ISO 3506-1 [4]
A2-50 / A4-50 500 210 Stainless, lower class ISO 3506-1 [4]

Nominal values from the standards. The supplier’s certificate states the class of the rod you receive.

Three points from site:

  • 8.8 only doubles the rod. The nuts, anchor and beam clamp must carry the same load. Pair 8.8 rod with nuts of at least class 8.
  • Stainless comes in classes. A class 50 stainless rod carries less than half of a class 70 rod of the same size (calculated on Rp0.2). Check the class on the certificate.
  • Hot-dip galvanised rod needs matching nuts. The zinc builds up on the thread, so use galvanised nuts that are tapped oversize [7].

A hanger is a chain: the fixing into the structure, the rod, any connector nut, the nut or channel nut under the channel, and the channel itself. The weakest link sets the safe working load of the whole assembly.

Link Indicative value Source
M10 rod, grade 4.8, factor 2 9.3 kN Rule of thumb (this page)
Universal beam clamp M10 4.5 kN Manufacturer data [5]
External 41 mm beam clamp with cone point screw M10 2.3 kN Manufacturer data [5]
Bent 41 mm beam clamp, single slot 1.0 kN Manufacturer data [5]
Ceiling anchor Per the anchor’s ETA Anchor manufacturer
Channel nut in 41 mm strut Not published in our sources Ask the supplier

Permitted working load per type, indicative; the manufacturer confirms.

In this example the rod carries two to nine times more than the beam clamp. Upsizing the rod therefore rarely gains anything. Look at the fixing first. Where you join two rods, use a connector nut to DIN 6334. Its length is three times the thread size, so both rods engage far enough [8].

How do you fix studding to concrete or steelwork?

In concrete, use an anchor with an internal thread: a drop-in anchor, a concrete screw with an internally threaded head, or a resin anchor with a threaded socket. Choose one assessed for cracked concrete, because the underside of a slab is normally in tension. On structural steel, use a beam clamp and leave drilling or welding to the structural engineer’s approval. In the UK, BS 8539 sets out how to select and install post-installed anchors and when to test them on site [9]. See ceiling anchors for threaded rod and the beam clamp guide.

What changes with long drops, side loads and fire?

  • Rod is a tension member. In compression it buckles. A side load bends it at the thread root, where it is weakest.
  • Brace where things move. Where cables are pulled through the route, plant vibrates or containment hangs long and low, brace the hanger with strut channel or an inclined rod. As a rule of thumb, brace from a drop of about 1.5 metres and wherever cables are pulled (rule of thumb, indicative).
  • Fire. For circuit integrity, manufacturers design with much lower stresses in the rod. Use only the tested combination.
  • Locking. Fit a lock nut or locking washer under the last nut so the channel cannot vibrate loose.

How does the configurator use these values?

In the trapeze module you choose M8, M10 or M12. The bill of materials counts rods, nuts, washers and ceiling fixings per tier. The rod capacity sits next to your choice as an indicative value with its source, so you can see straight away whether the rod, the channel or the fixing governs.

Where do these figures come from?

  1. DIN 976-1, Gewindebolzen, Teil 1: Metrisches Gewinde (successor to DIN 975).
  2. BS EN ISO 898-1, Mechanical properties of fasteners made of carbon steel and alloy steel, Part 1: Bolts, screws and studs. Stress areas and property classes.
  3. ISO 261, ISO general purpose metric screw threads, general plan. Coarse pitch per size.
  4. BS EN ISO 3506-1, Fasteners: mechanical properties of corrosion-resistant stainless steel fasteners, Part 1.
  5. Eurostrut, beam clamp product pages with permitted working load. Accessed 19-11-2026. https://eurostrut.com/universele-balk-klem-m10-eg/ESP10 · https://eurostrut.com/balkklem-41mm-extern-met-kegelpunt-bout-m10-hdg/ES1271HDG · https://eurostrut.com/balkklem-gebogen-41mm-1-sleufgat-hdg/ES711HDG
  6. Vergokan, threaded rod DIN 976, grade 4.8, hot-dip galvanised, 2 m: maximum tensile load per size at safety factor 1.7, and weight per metre. Accessed 19-11-2026. https://www.vergokan.com/nl/kabeldraagsystemen/Montagesystemen/Montagetoebehoren/TIM
  7. Eurostrut, hex nut DIN 934, oversize tapped, hot-dip galvanised. Accessed 19-11-2026. https://eurostrut.com/din-934-zeskantmoer-m5-overmaats-tv/934TI05
  8. DIN 6334, Hexagon nuts with a height of 3 d. Product example: https://eurostrut.com/din-6334-koppelmoer-m16-tv/6334TI16
  9. BS 8539, Code of practice for the selection and installation of post-installed anchors in concrete and masonry.

Frequently asked questions

How much weight can M10 threaded rod hold?

M10 has a tensile stress area of 58.0 mm² (ISO 898-1). In grade 4.8 with a safety factor of 2 that gives an indicative 9.3 kN, about 950 kg. Grade 8.8 doubles it to 18.6 kN. That is the rod alone; the fixing into the structure usually sets the real limit.

What is the difference between threaded rod and studding?

None. Studding is the common UK name for threaded rod, and allthread is the US term. All three describe steel bar threaded along its full length, usually to DIN 976-1, in lengths of 1, 2 or 3 metres.

Should I specify M10 or M12 studding for a trapeze hanger?

Work out the load per rod first. For most single and two-tier trapezes the rod has a large margin and the anchor or beam clamp governs. Choose M12 when that fixing is rated for it, when the drop is long, or when the manufacturer's data for the complete hanger asks for it.

Can threaded rod take compression or side load?

Not reliably. Threaded rod is a tension member. In compression it buckles, and a side load bends it at the thread root. Where cables are pulled, plant vibrates or drops are long, add bracing in strut channel or use a rigid channel upright.

Next step

See your own range in 3D.

In 30 minutes we show how your installers configure, what arrives on your side and what the client version on your range involves.

Manufacturer or wholesaler

Book a demo with Ismail

You see the configurator in your own brand and we discuss your range, systems and markets.

Reply from Ismail within one working day

Installer

Configure for free

A trapeze, frame or tray with cables in a few minutes, with a bill of materials and drawing.

Enquiry goes to a supplier · reply within one working day